This is a quote from part of a paper prepared for a class:
See any errors ?
For example, a 75 kva 3 phase 480 to 208Y/120 transformer can be protected with a primary
overcurrent device rated at 125 amps (75000/480 X 1.732 = 90 X 1.25 = 112 next size = 125) with no specified secondary protection OR the transformer can have a primary overcurrent
device rated at 225 amps (75000/480 X 11.732 = 90 X 2.5 = 225) IF your secondary protection
does not exceed 300 amps (75000/208 X 1.732 = 208 X 1.25 = 260 (300 = next size up)
See any errors ?