    I do not know if anyone can help. I have been using Mike Holt's Master Exam Prep and noticed that all his residential service calculation examples/questions do not include the addition of 25% of the largest motor into the calculation. Any reason for this? Perhaps this item is not asked on the PSI Master Exam.

    Any thoughts?

    Thanks

    #2
    Does the calculation start with an MCA value for the unit containing the motor? Unlike the FLA the MCA already contains the 25% increase.
    I do not have a copy of the exam prep to check out myself. Have you looked at the online addendum listing for the package?

    Comment


      #3
      Originally posted by Squantum View Post
      I do not know if anyone can help. I have been using Mike Holt's Master Exam Prep and noticed that all his residential service calculation examples/questions do not include the addition of 25% of the largest motor into the calculation. Any reason for this? Perhaps this item is not asked on the PSI Master Exam.

      Any thoughts?

      Thanks
      I used the Holts book electrical exam prep for my RW JW ME License class, (people taking each exam were in the same class) the instructor noted the addition of 25% is not in the book and made sure we added 25% of largest motor to all calculations on our own.