20 amp single receptacle
sparky1118
Massachusetts
Master Electrician
Good morning everyone. I’m a bit groggy and attempting to study for my masters. I’m using a exam prep book and I am confused on a question. So the question is “what is the ampere rating for a single receptacle on an individual branch circuit rated at 20 amps” now I thought that if you’re using a single receptacle on a dedicated 20 amp circuit it has to be a 20 amp outlet?
sparky1118
Massachusetts
Master Electrician
Thank you. I’ve found so far four questions that have the wrong answers in this book...
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Here is what the nec states
210.21 said:
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A
single receptacle installed on an individual branch circuit shall
have an ampere rating not less than that of the branch circuit.
infinity
New Jersey
Journeyman Electrician
Yes, a 20 amp single receptacle is the minimum size permitted on a 20 amp circuit, you could use a 30 amp or a 50 amp if you so choose.
kwired
Electron manager
NE Nebraska
You can put a single 15 on a 20 AMP circuit but not the other way around.
Sent from my SM-T350 using Tapatalk
I believe that's incorrect; a duplex 15, yes.
You can put a 15 amp single receptacle on a 20 amp circuit, as long as it is not a circuit with a single outlet (Individual Branch Circuit - per art 100)
Also agree you could use a 30 or 50 amp receptacle and would not be in violation of NEC.
growler
Atlanta,GA
They know what they are doing. You will remember those four questions for the rest of your life.
Just kidding it's probably a mistake but you will remember those questions.
marco_polo
USA
I’m confused after reading this thread, what I’ve usually been told to do for, for example, dining rooms, is have a 20 amp circuit in #12 romex and use regular 15 amp decora outlets. Would this not be to code?
kwired
Electron manager
NE Nebraska
If you have a single 15 amp duplex receptacle on a 20 amp circuit you have two outlets, therefore not a circuit with a single outlet and you are not required to use a 20 amp receptacle.
Basically the only time you must use a 20 amp receptacle is if you have a circuit serving a single outlet. Other than that it is your option to use 15 or 20 amp receptacle(s).
david luchini
Connecticut
Engineer
That's one outlet, not two outlets. Multiple receptacles, but a single outlet.