Jessehop said:In preparing of the exam I had a question that read...What is the ampacity of six current carring 4/0 xhhw conductors in a slab (wet location)?
none of the answers I came up with were in the multiple choice. How do you figure this?
infinity said:What did you come up with? 416 amps?
infinity said:I assumed XHHW-2. I should have read the OP more closely.
4/0 CU XHHW (75 degrees in wet location) = 230 amps * 2 sets * 80% = 368 amps.
4/0 CU XHHW-2 (90 degrees in wet location) = 260 amps * 2 sets * 80% = 416 amps
Pierre C Belarge said:Dennis
It could be 416 amp if this is single phase, I believe you may be thinking 3 phase.
infinity said:Dennis I agree more with your answer. For some reason I got stuck on the concept of a parallel feeder in the same conduit. Clearly the question didn't say that.:roll:
danickstr said:I would have assumed that it meant 6 conductors on one phase and derated based on 6 conductors in a conduit.
edit answer 1248 amps
I couldn't help but interject the possibility which :roll: there were no poor questions just some that make us think more than others.:wink:Dennis Alwon said:We can assume all possibilities which only gives credence to a very poor question. Since Jesse has not responded with the choice of answers or anything else I guess we won't ever know.
Inspectorcliff said:I couldn't help but interject the possibility which there were no poor questions just some that make us think more than others.