I have a queston on a practice test that i got wrong maybe someone can help me.. this question reads
" A store building measures 60ft by 80 ft and is supplied by a 240/120V 3 phase 4 wire delta system.. which of the following is the minimum allowed number of 2 wire, 20 ampere branch circiuts required to supply the genral lighting in this building?"
A) 6
B) 7
C) 8
D) 9
I got 60x80=4800sq ft times 3 VA (table220.12) = 14400VA divide by 120v = 120A divide by 20A = 6 circuits but is wrong.. the answer key says C) 8 but the key could be wrong
i thought maybe cuz of 3 phase that i would divde by 120* 1.732 but you get a lower number ofcourse...