Announcement
Collapse
No announcement yet.
Oven and microwave on same 30A oven ckt?
Collapse
This topic is closed.
X
X
  • Filter
  • Time
  • Show
Clear All
new posts
    searched and no posts with ovens in the title so...
    nothing says you can't put an oven and a cooktop on the same circuit. i know you can put an oven and a cooktop on a 50A circuit, but those two take alot of juice. i have this customer that bought a 240V microwave that takes 15A. the oven says it takes 17. i know that is 32A because i can do simple addition, and i know 10g wire is good for at least 35A. i also know i can't fuse the 10g at more than 30A.
    WHAT says i can't supply them both from the same circuit? are they continuous loads? is there no reductioins, like with multiple ranges or dryers? i am sure there is something that wont let me do it, and am planning on running a new 240 ckt tomorrow. (the stupid micro requires a neutral!).
    the reason is the customer told me to run a 20A 120 for the micro above the 30A oven outlet, which i did. but it is of no use now since fool customer went out and got this 240V micro. it is NOT a Bosch, which lets you feed one from the other, either. they are both kitchen aid. and dig this: Kitchen Aide (whirlpool) factory HAS NO, ZERO, TECH SUPPORT!!!!! all they have is NO instructions for this with the micro, but the oven DID have instructions saying to put it on it's own circuit breaker.
    The End of the World as i Knew it: 2012. I'm having my Doom's Day now.
    #2
    In practice it should work fine, and be safe, but I feel that it would a violation on at least two counts.
    Firstly the instructions with the microwave say to put it on its own circuit, and not following this instruction is probably a violation.
    Secondly, for what maximum OCPD is the microwave listed ? Almost certainly less than 30 amps I suspect. Probably 15 or 20 amps, in which case connecting an appliance to a larger OCPD than specified is likely a violation.
    Does the microwave oven actually USE 15 amps ? or is it designed for a 15 amp circuit ? with an actual current draw of less than 15 amps.
    15 amps at 240 volts is an awfull lot for a microwave oven ! very large ones in the UK seldom exceed 13 amps at 240 volts.
    If it does actually use a full 15 amps, then the total load on the branch circuit is more than 30 amps. I would not consider either appliance to be a continous load, so the branch circuit can be loaded to 100%, but in this case the load is more than 100 %
    Should be fine in practice, but strictly correct ? I think not.
    Comment
      #3
      FWIW a cooktop and oven combination under code are assuming they are both built-in units, essentially amounting to the load equivalent of one freestanding range.
      Is the microwave a countertop appliance or built-in unit?
      If the microwave is cord-and-plug connected, you will likely be limited to a circuit rating not higher than the matching receptacle rating... and as mentioned, you cannot knowingly put a greater load on the circuit than what it is rated.
      I will have achieved my life's goal if I die with a smile on my face.
      Comment
        #4
        It always amazes us that kitchen remodels NEVER seem to have the correct appliance and cabinet details when roughing them in, and then its up to us, the electrician to redo all of our work often at a reduced cost because of their failure to communicate the changes.
        The thing that drives me the most crazy is that the customers will spend $2,000 on microwave convection oven and then whine and moan about the $300 to run the circuit and hook it up.
        Lately when estimating kitchen remodels we are very specific that it is an estimate and the job will be billed at time and material, because there are so many additions, changes, hidden factors, extra trips, things not ready when we are told to be there etc.
        It is very easy to overrun a $2000 kitchen electric rewire / remodel by $1000, by the time it is done, and that is still less than they paid for the crappy refrigerator.
        Comment
          #5
          My thoughts are that since you said you ran a dedicated 20 amp (120 volt) circuit already, why not just change that circuit to a 240 volt circuit and use it?
          I live for today, I'm just a day behind.
          Comment
            #6
            most of them require 4 wire. Not like the ovens and cooktops that can be wire 3 or 4 wire.
            Comment
              #7
              Well he said it was 240 volt, if he would have said it was 120/240 volt that would have clarified things a lot. I have never seen such a unit, so I do not know what the "norm" is.
              Comment
                #8
                $2000 for a kitchen remodel? That sounds VERY barebones... Last large kitchen I did cost about the same as their range I can't even imagine doing a small kitchen for that price unless hardly anything is changing.
                Peter A.
                Comment
                  #9
                  That doesn't help get your point across IMO, you can get a range for as little as a couple hundred dollars or spend ten thousand or even more in some instances maybe.
                  Add: I haven't went looking at ranges at the consignment stores for years now but you used to be able to get one for maybe only twenty bucks, but it was definitely not the latest in style.
                  Comment
                    #10
                    These are not large kitchens or homes most built in the 70's + 80's under 2000 sq ft. Usually new cabinets, change and add some recpts, recess can or 2 etc
                    They can be roughed by 1 guy in a day or less and trimmed in 1 day or less if things are complete and ready
                    Comment
                      #11
                      We do not have enough information to answer the question directly.
                      For demonstration purposes let's assume it complies. If this were your home would you do that? I know I would not as that would be a poor practice and asking for trouble.
                      Comment
                        #12
                        Still, unless there is hardly any cabinets at all even some really cheap ones will eat up most of 2 grand in cabinets alone - and they are often replacing countertops and sink as well. Whoever is doing this probably wants a little labor on top of it even if he is cheap.
                        Comment
                          #13
                          That is just the electric, my point was the customers spend more for a single appliance than for all of the electrical including the permit.
                          Comment
                            #14
                            thanks for the replies. the microwave has to be hard wired as there is a whip with four wires in it, they look to be 14g at best. i am pretty amazed that it will draw 15 amps (it says it uses 3600 watts) at 240, so.....i guess that would get around any load/recept issues. also the oven has a whip as well with i believe 12g wires
                            if it were my house, i don't know, i guess i would wire it up and do an actual voltage draw on it first. i expect it to be less, but then maybe the oven, if i did the same, would be more, don't have any 240 extention cords laying around. but i guess maybe that is the only way.
                            btw this is a new house w/a change order. attic above is accessible, i left a 1"pipe from the panel to the attic so it's very doable. just that it's already had 20" of fluff blown in. i tend to run a pipe to the attic in every new house i do, just in case! make sure to use a cap or duct seal.
                            also broadbase, it was the oven that said it should be on it's own ckt, not the micro, but it makes no difference. but then, check this out, in the ovens directions it says it can share a circuit with an list of cooktops! so... what does THAT mean? And in that note it does NOT say what the size of that ckt must be!! and after two calls to kitchen aid, to get the BS that they have NO TECH support for me, really just sent me off the deep end. i cussed out both of the two gals who gave me lip that i wasn't allowed to call their tech line unless i was a certified installer. well, happy thanksgiving beaches!
                            Comment
                              #15
                              The 14ga whip conductors rules out feeding from same circuit as oven. The only permitted tapping of a household cooking appliance circuit requires 20A conductors, including whip conductors, and the circuit must be rated 50A. See 210.19(A)(3) Exception No. 1.
                              Comment
                              Working...
                              X