Transformer Overcurrent Protection Table 450.3(B)

Status
Not open for further replies.

Grendal

Member
According to NEC Table 450.3(B), for more than 9 amps for primary and secondary protection; the primary protection max is 250% and the secondary protection is sized at 125% max of the transformer rated current.

Is there any issue sizing both the primary and secondary at 125%? When doing renovation projects sometimes we try to reuse the existing conduits and wiring to save money. So the primary side might end up being only 125%.

Is there a rule of thumb that if you size the secondary at 125% the primary should be at least XXX%? Understand that there are different types of breakers and many breakers you can adjust the trip curves.

Any help would be appreciated.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
According to NEC Table 450.3(B), for more than 9 amps for primary and secondary protection; the primary protection max is 250% and the secondary protection is sized at 125% max of the transformer rated current.

Is there any issue sizing both the primary and secondary at 125%? When doing renovation projects sometimes we try to reuse the existing conduits and wiring to save money. So the primary side might end up being only 125%.

Is there a rule of thumb that if you size the secondary at 125% the primary should be at least XXX%? Understand that there are different types of breakers and many breakers you can adjust the trip curves.

Any help would be appreciated.

You can use 125% for the primary conductors and OCPD and this is the norm for most installations. The code does not require 250% on the primary, rather it is allowed when certain conditions require it.
 

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
The reason you're allowed to go up to 250% on the primary ocpd is to accommodate transformer inrush, which is typically listed as 8-12 times the fla, but with more efficient transformers, can be much higher. The downside to the 250% number is that your cabling now has to be at that ampacity.
There is no "rule of thumb" for the sec'y breaker, just be sure to protect the load conductors.
 