Saint Germain
- Louisiana
Hello all,
I am trying to size a 120 VAC UPS. Typically, all of my devices are 120V and I know either the VA or Watts so I would convert Watts to VA and add all of the VA's together to size the UPS. This time some of my devices are 24 VAC, which I will have a 120/24 VAC transformer for.
I am getting stuck with trying to calculate the total VA for the devices that are 24 VAC. The data sheet for these devices state 72 VA at 24 VAC. How can I find the VA for these devices @ 120VAC?
This is what I have calculated, but I need someone to please tell me where I am going wrong here.
24V - 72VA
1. Find current 72VA / 24V = 3.125A
2. Find resistance of device 24V / 3.125A = 7.68 Ohms
3. Find current @ 120VAC with resistance being constant 120V / 7.68 = 15.625A
* I think this is not correct..shouldn't the current be lower with a higher voltage??
4. Calculate VA @ 120V 120V * 15.625A = 1875VA
Thanks for your help,
Saint Germain
24V - 72VA
Saint Germain