I have equipment that contains refrigeration compressors. Generally, I will always use the rated HP and RLA (rated load amps) to list on the fuse label.
The equipment I am looking at now has a CPR valve that will limit the compressor capacity. The compressor manufacturer publishes data on the Running Load Amps for the this capacity, as well as the kilo-watt data at this capacity. There is not a published HP rating at this capacity.
Is it permissible to use the amps that the compressor manufacturer publishes for the controlled capacity, or do I have to use the Rated Load Amps?
Would I then be able to turn the KW data into HP and use that on my fuse label?
The manufacturer does not list the RLA on the nameplate of the compressor. They only list the LRA.
The equipment I am looking at now has a CPR valve that will limit the compressor capacity. The compressor manufacturer publishes data on the Running Load Amps for the this capacity, as well as the kilo-watt data at this capacity. There is not a published HP rating at this capacity.
Is it permissible to use the amps that the compressor manufacturer publishes for the controlled capacity, or do I have to use the Rated Load Amps?
Would I then be able to turn the KW data into HP and use that on my fuse label?
The manufacturer does not list the RLA on the nameplate of the compressor. They only list the LRA.