- Chapel Hill, NC
- Retired Electrical Contractor
If I took 2 - 60 watt electronic low voltage transformers (120V- 12V) and hooked them up in parallel, what would happen? Would I get 120 watts out of it???
141211-1052 EST
Dennis Alwon:
What is a "60 watt electronic low voltage trany"?
Is this an AC or DC output? If AC how close to a sine wave is the output?
If AC is the waveform synchronized to the input AC waveform?
If synchronized that also implies exactly the same frequency, but not necessarily no phase shift.
If AC output my guess is that paralleling can be a major problem.
141211-1052 EST
Dennis Alwon:
If the output is AC I don't think 'or-ing' diodes would be a solution.If these 'transformers' are actually electronic switching power supplies, then unless they have been designed for parallel operation, they will likely let out their magic smoke when operated in parallel.
You might be able to get around this by using 'or-ing' diodes to parallel them...but might have better results simply splitting your loads so that each transformer has a separate load.
-Jon
In which case I don't think it will work.Ac input and output. This is a standard trany for low voltage lighting
-Jon
Told ya so!!!No real smoke but the tranies are now toast.
Told ya so!!!
Yes, but I couldn't resist.............No- you said I don't think...... not the same as it wont work...
If they were truly identical AC magnetic transformers (identical turn count), then paralleling should be fine as long as correctly phased. But it may be more likely that they used phase controlled SCRs to provide a non sine wave 60V RMS AC.No real smoke but the tranies are now toast.
In that case small component value differences could cause serious problems since the output waveforms would not be identical and an output circuit not expecting to be back fed would likely open smokelessly.
I did assume you guys were correct but I was hoping you weren't.Yes, but I couldn't resist.............