New EE
Member
- Location
- California
I have an existing Motor Control Center that I am trying to get a general idea of the existing load. The GE MCC is a 600A, 480V, 3PH, 3W, 8000 line/spectra Motor Control Center with a 3P400A main breaker.
My question is whether I am doing my calculations correctly just to get a general idea of the existing load. I put a power logger on for about 30 minutes and took the highest load readings during this timeframe.
Phase A: 241.7 x .480 = 116.0
Phase B: 244.3 x .480 = 117.3
Phase C: 243.4 x .480 = 116.8
116.0 + 117.3 + 116.8 = 350.1
350.1 / .831 = 421.3 Amps
Is this the correct way just to get an idea of the total existing load on the MCC? Note that the system is 480V, 3PH, 3W (not neutral)
Thanks.