Sizing motor branch circuit conductors.

Status
Not open for further replies.

JdoubleU

Senior Member
I know that you have to use the table in the NEC to size the motor conductors and not the name plate, I just can not remember why. Would someone be able to shed some light on this for me.


Sent from my iPad using Tapatalk
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The generally accepted reason is that at some time in the future the motor may be replaced with one of the same HP but different efficiency. If the circuitry is sized from s table which uses a worst case motor, then any replacement will be OK.
Now if the motor is part of a system, such as an A/C, you can assume that any replacement will be a match for the original. So, in those cases the appliance nameplate is authoritative, rather than the tables.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Who knows. There may have been a reason when the requirement was put in place or it may have been something that someone just decided would be a good idea.
 

JRW 70

Senior Member
Location
Eastern Central Missouri
Occupation
Testing and Engineer
Future Changes

Future Changes

Goldigger has the correct answer. The cables need to be
sized for the worst motor configuration possible for a given
horsepower rating
 