neutral

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is something you can read about non-linear loads -- pretty short- one page http://www.mirusinternational.com/downloads/hmt_faq01.pdf

http://www.uecorp.com/busway/uploads/docs/en/ue_neutralratings.pdf said:
Sources of non-linear loads are computer equipment with switched-mode power supplies, variable speed
motors and drives, photocopiers, laser printers, fax machines, battery chargers, UPSs, fluorescent light
ballasts, and medical diagnostic equipment
.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A typical building, even though is has those "harmonic" producing loads, doesn't normally have enough of those loads to require counting the neutral as a current carrying conductor.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's a brief summation on the neutral as a CCC:

Neutral Conductors:
Here's some examples of when to count and not count the neutral as a current carrying conductor or CCC:

3?- 208Y/120 or 480Y/277 volt system-different circuit types:
A) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
B) 3 wire circuit w/ 2 ungrounded, 1 neutral = 3 CCC's
C) 4 wire circuit w/ 3 ungrounded, 1 neutral = 3 CCC's*

Notes:
A) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
B) In this circuit the neutral current will be nearly equal to the current in the ungrounded conductors so the neutral counts as a CCC
C) In this circuit the neutral will only carry the imbalance of the current between the three ungrounded conductors so it is not counted as a CCC, with an exception, *if the current is more than 50% nonlinear (see below for NEC article 100 definition) then the neutral would count as a CCC.

1?- 120/240 volt system-different circuit types:
D) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
E) 3 wire circuit w/ 2 ungrounded, 1 neutral = 2 CCC's
Notes:
D) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
E) In this circuit the neutral will only carry the imbalance between the two ungrounded conductors so the neutral is not counted as a CCC.
Nonlinear Load. A load where the wave shape of the steady-state current does not follow the wave shape of the applied voltage.
Informational Note: Electronic equipment, electronic/electric-discharge lighting, adjustable-speed drive systems, and similar equipment may be nonlinear loads.
 