Good Morning Everyone,
EGC as GEC seems to be a hot topic that has been discussed in great depth already on this forum; unfortunately, I have not seen a definitive answer to my specific question so I thought I would spark a continued discussion now.
We use the same vendor for compressors on all of our sites and provide the same single line for each installation. The compressor MCC has a 5kVA 480/120V step down transformer to provide control power and 120VAC auxiliary power. Dozens of other sites have received inspector approvals, but this new site we're building is receiving push-back because we do not detail a connection back to a local grounding electrode (and didn't size a GEC).
I haven't personally inspected the other sites to know if the contractor knew to tie the transformer to a grounding electrode, but since no GEC was sized or called out in our drawing I would be surprised if they did. My question to everyone is am I correct in my current review that my transformer, a 5kVA 120V single phase secondary, is a separately derived system that requires a direct connection to a grounding electrode? I see that there is an exception for <1kVA transformers that is commonly used for control transformers, but I can't use that to justify no GEC for a 5kVA.
My second question is I thought that my EGC served dual purpose as an EGC connection, but after reviewing all of the previous topics I am not confident that this is a code compliant installation. The EGC run in the feeder for the control transformer is sized per table 250.66. Reading NEC 2014 250.121 makes me think that this isn't proper:
[CODE]250.121 Use of Equipment Grounding Conductors. An
equipment grounding conductor shall not be used as a
grounding electrode conductor.
Exception: A wire-type equipment grounding conductor installed
in compliance with 250.6(A) and the applicable requirements
for both the equipment grounding conductor
and the grounding electrode conductor in Parts II, III, and
VI of this article shall be permitted to serve as both an
equipment grounding conductor and a grounding electrode
conductor.[/CODE]
Chiefly, we aren't using Cadweld or permanent compression connections for the EGCs.
Tl;dr: Previous installations used the EGC as a GEC (sized per 250.66) but this isn't approved on a new site.
Final question/takeaway: Is there a summary of what exactly I would need to do to my EGC to use it as a GEC or is it just cheaper/easier to add a new GEC connection to a nearby grounding electrode?
EGC as GEC seems to be a hot topic that has been discussed in great depth already on this forum; unfortunately, I have not seen a definitive answer to my specific question so I thought I would spark a continued discussion now.
We use the same vendor for compressors on all of our sites and provide the same single line for each installation. The compressor MCC has a 5kVA 480/120V step down transformer to provide control power and 120VAC auxiliary power. Dozens of other sites have received inspector approvals, but this new site we're building is receiving push-back because we do not detail a connection back to a local grounding electrode (and didn't size a GEC).
I haven't personally inspected the other sites to know if the contractor knew to tie the transformer to a grounding electrode, but since no GEC was sized or called out in our drawing I would be surprised if they did. My question to everyone is am I correct in my current review that my transformer, a 5kVA 120V single phase secondary, is a separately derived system that requires a direct connection to a grounding electrode? I see that there is an exception for <1kVA transformers that is commonly used for control transformers, but I can't use that to justify no GEC for a 5kVA.
My second question is I thought that my EGC served dual purpose as an EGC connection, but after reviewing all of the previous topics I am not confident that this is a code compliant installation. The EGC run in the feeder for the control transformer is sized per table 250.66. Reading NEC 2014 250.121 makes me think that this isn't proper:
[CODE]250.121 Use of Equipment Grounding Conductors. An
equipment grounding conductor shall not be used as a
grounding electrode conductor.
Exception: A wire-type equipment grounding conductor installed
in compliance with 250.6(A) and the applicable requirements
for both the equipment grounding conductor
and the grounding electrode conductor in Parts II, III, and
VI of this article shall be permitted to serve as both an
equipment grounding conductor and a grounding electrode
conductor.[/CODE]
Chiefly, we aren't using Cadweld or permanent compression connections for the EGCs.
Tl;dr: Previous installations used the EGC as a GEC (sized per 250.66) but this isn't approved on a new site.
Final question/takeaway: Is there a summary of what exactly I would need to do to my EGC to use it as a GEC or is it just cheaper/easier to add a new GEC connection to a nearby grounding electrode?