marmathsen
- Seattle, Wa ...ish
- Electrical Contractor
https://i.imgur.com/Wj6rAZG.png
I'm hoping some of you guys and gals can help me figure this out. Attached is an image I drew up of how I THINK it should be connected but please correct me if warranted.
I have a potential customer who has asked me to run a feeder to a detached shop on a residential property - No big deal. Then she tells me that they want me to setup provisions for a portable 7kW generator that will be stored and operated inside the shop and feed back to the main house for backup power. I have spent many hours now trying to get to the bottom of what the NEC requires (I'm using 2017 edition, and I'm in Snohomish County Washington). It is a non separately derived system because the neutral is permanently bonded to utility neutral.
One hangup I'm having is that the generator has a neutral to equipment ground bond that I'm not inclined to disconnect, but by not disconnecting it, don't I create a parallel neutral current path on the raceways and enclosures?
If I do "un-bond" the neutral to EG connection then I'm inclined to say I should dismantle the other 20A GFCIs on the side of the generator because the manual explicitly says they won't function properly if it's disconnected.
Look forward to hearing back from everyone.
Side note - I did express concerns about operating a gas engine inside an enclosed space and she was trying to assure me that her husband will "properly" seal and vent it so it shouldn't be a concern. I will be STRONGLY recommending that they install a CO alarm in the shop.
Rob
Rob