    Generator Installation

    I have to retrofit a generator house to fit two generators however space only allows me to fit the two generators end to end and not side by side.

    Has anyone carried out an installation like this before? Are there any code restricting this?

    Both generators will be running simultaneously, is it better to face the two radiators towards each other and is tall an exhaust system or turn both generators in the same direction with an exhaust system?

    #2
    I don't know about code
    I would face them both with the radiator out and bring cooling and combustion air in from the middle of one side and exh out the other (perhaps out the roof)

    you do not want the radiators blowing into each other

    Comment


      #3
      Originally posted by Ingenieur View Post
      I don't know about code
      I would face them both with the radiator out and bring cooling and combustion air in from the middle of one side and exh out the other (perhaps out the roof)

      you do not want the radiators blowing into each other
      In specific answer to the OP's suggestion, as long as there is sufficient clearance between them for lateral air flow you can put both radiators facing each other (which does not mean blowing at each other). Provide air inlet at the center and individual cooling air exhaust at each end.
      That way the air that has been through each radiator can go on to help cool the engine directly.
      If you put the radiators at opposite ends you will need to arrange two end feeds and a center exhaust. In addition the two air streams will be opposing each other at the center, for a lot of turbulence.

      Sent from my XT1585 using Tapatalk

      Comment


        #4
        this may help
        pg 17
        http://s7d2.scene7.com/is/content/Ca...13-53120-44971

        for engine mntd cooling the fans pull cool air over the engine and alternator and blow thru the radiator
        the cool intake air also provides the combustion air
        blowing hot air into the room and over the engine and alt is probably not a good idea
        Last edited by Ingenieur; 06-11-18, 06:56 PM.

        Comment


          #5
          Originally posted by Ingenieur View Post
          this may help
          pg 17
          http://s7d2.scene7.com/is/content/Ca...13-53120-44971

          for engine mntd cooling the fans pull cool air over the engine and alternator and blow thru the radiator
          the cool intake air also provides the combustion air
          blowing hot air into the room and over the engine and alt is probably not a good idea
          Thanks, I did not realize that was the air flow direction. Vehicle mounted engines mainly use the opposite flow because of the availability of ram effect air while the vehicle is moving, I guess.

          Comment


            #6
            Originally posted by GoldDigger View Post
            Thanks, I did not realize that was the air flow direction. Vehicle mounted engines mainly use the opposite flow because of the availability of ram effect air while the vehicle is moving, I guess.

            exactly
            and to evacuate the engine compartment heat
            and aero reasons
            plus drawing air in from the relatively sealed engine compartment and out the front would need a healthy fan

            smart fans on newer cars actually shutdown at times to conserve fuel

            Comment


              #7
              Assuming the air outlets are facing each other, I've seen the use of upward draft directional housings or addons. With drains and protective grates.

              If in or near a residential area, there could be sound attenuation required.

              Proper fin spacing on radiators if ordering new generators, should be considered.

              Sent from my LGMP260 using Tapatalk

              Comment


                #8
                I would set them alternator to alternator (radiators on the outside wall) and exhaust over the radiator like shown in the figure in the link
                I would bring in air from the center of the space (I would have 2 inlets w/auto dampers, each sized for 1 gen, cooling AND combustion air, and interlocked) I would duct it to sweep over the alternator and engine and out the radiator

                Comment