I am working on a similar project and have had same question.
Example you have deep fryer and coffee/tea maker in the list. To me these are continuous loads and they will be on more than 3 hours. So I did not apply 220.56 demand factor to those.
I like to be liberal on my design and safe, so what I did what everything in the kitchen I multiplied by 1.25 as all continuous loads.
A restaurant/deli will be on about 12 hours a day and tell me which coffee machine wont be on more than 3 hours.
Here is the objection will be coming from other forum members if any; continuous load means using Max current more than 3 hours. There is the argument, deep freezer or coffee machine will be on more than 3 hours, but do they use Max current continuously more than 3 hours. I said yes to this question and made engineering recommendation to my client to upgrade the existing service to accommodate the renovation. Now it is up to the client.
Restaurant or deli, everything in the kitchen will be used more than 3 hours and everything will use a lot of current. Instead of picking max current or 3 hours or not 3 hours I totally ignored the table 220.56 which I believed the right thing to do.