LibertyEngineering
- Allentown, PA
Good Evening,
I am working on a fire pump feed where we need to provide the ATS for the fire pump controller. It is not included with the controller.
I will be serving the normal side of the ATS via a separate utility company service. It is a 480V 3 phase 40HP Pump. Locked Rotor is indicated as 290A . Since I cannot route the service outside the building I will be adding the allowable OCP in the service disconnect and run it as a feeder with the listed fire rated cable through the building. Sizing the OCP for locked rotor means I will need 300A time delay fuses.The actual runnig Load Amps of the motor is marked on the motor as 42A. My question is since the actual RLA of the motor is only 42A Can I use a 100A transfer switch or since the OCP is set at 300A do I need a 400A transfer switch? I do not see anything about sizing the ATS.
Thanks for any comments!