480 VAC, 3∅ Distribution Question

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • Bretzel
    replied
    Originally posted by LarryFine View Post
    Perfectly normal readings for an ungrounded system.

    You're not seeing 277/277/277 because the meter loads each line slightly as you test it. A low-impedance tester should show much less each time.

    That's my theory.

    That sounds reasonable. We did find several Wye connected motors both on our 480 primary voltage and on the 208 side of transformers. We also found a few Wye transformers in the mix. We conducted a complete survey of the entire system nearly down to the last outlet. It was exhaustive and mind boggling how wrong some of the things we found were. Simple things ~ 50 amp double pole breaker feeding a single 14ga conductor AND a white one at that! We hired an additional electrician to start straighten in it out.

    Leave a comment:


  • kwired
    replied
    Originally posted by LarryFine View Post
    The floating system will tend to settle around wye voltages due to capacitance with the world.

    That explains why your line-to-ground voltages were what they were, and not zero.
    I agree.

    Originally posted by Bretzel View Post
    Does a delta system produce 277? I thought that was a flavor produced by a Wye system.
    If you have wye configured loads (many common smaller 9 lead motors are wye connected) and happen to have a ground connection to the wye point (intentional or not) you will have reasonably solid ~277 volt to ground readings on said system. But any other wye connected load can do same thing. Most transformer primary circuits will be delta and won't be an issue, but if you happen to have a wye primary or reverse feed a delta-wye transformer, be sure to leave the primary side neutral "floating".

    Leave a comment:


  • ptonsparky
    replied
    Originally posted by Bretzel View Post
    It has been a long, long battle but we have located two major ground fault and one minor one, all on the same leg of the system. One fault was in an abandoned building. We simply cut power to the building and will deal with it if and when the facility is required in the future. Another fault was in an underground PVC conduit near a metal tower which rises some 60' above average terrain and appears to be ungrounded as it is sitting on concrete piers and has no ground rods. The final one is somewhere in an overhead line heading out to the far end of the property. With these faults cleared or simply off-line we have more normal voltage readings. Phase to phase is 480 volts anywhere on the system. On this 480 volt, ungrounded delta system we should be seeing 480 between each phase and ground. We are seeing 229, 226, and 220 to ground.

    Any thoughts on this situation?

    Thank you in advance.

    Thanks again for coming back.

    Leave a comment:


  • LarryFine
    replied
    Originally posted by Bretzel View Post
    Does a delta system produce 277? I thought that was a flavor produced by a Wye system.
    The floating system will tend to settle around wye voltages due to capacitance with the world.

    That explains why your line-to-ground voltages were what they were, and not zero.

    Leave a comment:


  • Bretzel
    replied
    Originally posted by LarryFine View Post
    Perfectly normal readings for an ungrounded system.

    You're not seeing 277/277/277 because the meter loads each line slightly as you test it. A low-impedance tester should show much less each time.

    That's my theory.

    Does a delta system produce 277? I thought that was a flavor produced by a Wye system.

    Leave a comment:


  • LarryFine
    replied
    Originally posted by Bretzel View Post
    Phase to phase is 480 volts anywhere on the system. On this 480 volt, ungrounded delta system we should be seeing 480 between each phase and ground. We are seeing 229, 226, and 220 to ground.

    Any thoughts on this situation?
    Perfectly normal readings for an ungrounded system.

    You're not seeing 277/277/277 because the meter loads each line slightly as you test it. A low-impedance tester should show much less each time.

    That's my theory.

    Leave a comment:


  • Bretzel
    replied
    Faults Located!!

    It has been a long, long battle but we have located two major ground fault and one minor one, all on the same leg of the system. One fault was in an abandoned building. We simply cut power to the building and will deal with it if and when the facility is required in the future. Another fault was in an underground PVC conduit near a metal tower which rises some 60' above average terrain and appears to be ungrounded as it is sitting on concrete piers and has no ground rods. The final one is somewhere in an overhead line heading out to the far end of the property. With these faults cleared or simply off-line we have more normal voltage readings. Phase to phase is 480 volts anywhere on the system. On this 480 volt, ungrounded delta system we should be seeing 480 between each phase and ground. We are seeing 229, 226, and 220 to ground.

    Any thoughts on this situation?

    Thank you in advance.

    Leave a comment:


  • drktmplr12
    replied
    OP delivered.

    Nice.

    Leave a comment:


  • __dan
    replied
    Thank you so much for the feedback and update(s). I'm sure a lot of guys are learning a lot here.

    Certainly it was long past time for a survey. It's hard to find someone with a good mind for the technical problems you have. Just gaining an understanding is a big improvement. Most guys will look at what you have and tell you the breaker will trip if there's a problem. With the floating system, the breaker does not trip when you expect it to.

    The site contiguous EGC, really it's there to limit voltage differences between metal parts and structures during fault and normal use conditions. Probably the single best improvement you could make regarding avoidance of future catastrophe. An investment in the avoidance of far bigger future costs.

    Just a working premise, but I would look at the drives connected to the floating Y system. I am curious. It's a good bet some or most were installed without concern for floating the drive front end, at the internal input grounding screw.

    Leave a comment:


  • ptonsparky
    replied
    One last question...does the EE wear suspenders or did you manage this on you own?

    Leave a comment:


  • ptonsparky
    replied
    Sounds like you have it under control and headed in the right direction.

    Thank you for filling us in on your progress.

    Leave a comment:


  • Bretzel
    replied
    We found the ground fault to be in one section of the plant; an area of about 4 acres. Within this area the feeders form a loop. It appears to have been configured in such a manner to allow for shutting down blocks of service while maintaining service to the rest of the area. Nothing the POCO doesn't do. However, some of the switch gear is circuit breakers and fused switches rather than simple switches. I understand the thinking for the blocks and for the protection but I don't think the circuit breakers or fuses would act any as automatic overload protection should the entire loop be energized, as it was. Keeping the loop from being fully energized is now a procedural issue after repairs are made.

    The loop itself is not the cause of the ground fault. However, in the process of investigating the loop , we found the appearance of two separate faults on the same leg within the loop. In our inspection process we shut down one block where the overhead lines were ancient, had rotting crossarms and were in close proximity to a metal structure. We found no evidence of the lines having arched against the structure but the lines had enough slack to do so in a strong enough wind. We removed these lines altogether. We tested for faults before restoring power to the area and found none. We closed one switch and the fault returned. We opened this switch and closed the switch feeding the other end of the now former loop. A fault appeared on that end as well. We have been through the 480 side of the rest on the system in this area. There is one building fed underground through 60 year old pipe on the north end of the loop. That feeder is my prime suspect for the fault at this time. We'll are planning a shut down in that area in the coming weeks. If the building service isn't the problem then we have to start looking into the secondary side of everything in the area.

    The other end is all newer work; underground in 3" conduits. We lines we removed were the first section of original lines where this new work comes out of the ground at one end of the loop. This newer work has three underground vaults along it's path. We are planning on a shutdown which will allow us to open the vaults and see what is going on in them. My first concern is that there are three line sets at the beginning but only one is currently in service. Two of the line sets are 3 wire 500 mcm with a bare ground wire that appears to be 3/0. The third set of 3 runs of 750 mcm, 15Kv cable with a 3/0 ground cable. The service starts on one set of the 500 mcm cable but ends up on the 15kV cable at the other end! I am assuming, which may be completely false, there is a good reason for this such as a cable went bad and someone switched it in a hasty repair. I have bandaids on turnicates on plaster casts. How do you eat an elephant? One bite at a time.

    It looks like someone was thinking about bringing the primary all the way through the plant (this point is about as far as it gets from the substation) instead of having a substation at the POCO entry point. The work looks to be about 18 years old given the production dates on the wire and conduit. It is some of the best workmanship on property but there are zero records of who did it or why. It appears there was some work done about 10 years ago by the same company which contracts with the POCO for line work when the POCO crews are two busy.

    I have convinced management to install a fourth wire on all of the 480 distribution and to replace the antique substation entirely. We are working with the POCO to supply us with a 480 volt temporary feed while the substation gear is removed, the PCB contaminated concrete floor is demoed, the structural brick repairs are completed, a new roof is installed, and the POCO brings in a new permanent underground primary service for us.

    I did follow one contributor's recommendation and picked up a refurbished 3M fault detector.

    I'm going to have to ask for an increase in my vodka budget.

    Leave a comment:


  • Wire-Smith
    replied
    Originally posted by Russs57 View Post
    Couldn’t we run around the plant with an a amprobe and see which of the three phase conductors don’t sum to zero?

    Asking because I have limited experience in non standard systems.
    every facility even underfunded ones with ungrounded or resistance grounded systems that i have been too have a ground fault locator (you can buy used ones cheap) it's a toner you follow where the tone gets louder and you can find the fault easily.

    if there's only one unintentional ground connection (some might call a ground fault) on an ungrounded system there will not be current flow on the ground. if there's 2 different phase conductors unintentionally grounded, there will likely be opening of ocpd if bonding is proper/adequate.

    Leave a comment:


  • __dan
    replied
    Originally posted by Russs57 View Post
    Couldn’t we run around the plant with an a amprobe and see which of the three phase conductors don’t sum to zero?

    Asking because I have limited experience in non standard systems.
    The system discussed here, there is no guarantee the metal enclosure is safe to touch to open and Amprobe.

    You could bang 3 ft of pipe in the ground at an assumed remote earth, tie 500 ft of #12 thhn to that and run around with a voltmeter to see if you can measure a voltage difference from the remote Earth probe to *any* metal, elec equipment, gates, metal siding, I beams ...

    Next would be making a list of all the drives on the floating supply, gathering their factory instructions, and opening them looking for the bonding screw (maybe after checking to see if the enclosure is not at a voltage level above Earth).

    Not a time to get adventurous. Get management to sign off on the next procedure.

    Leave a comment:


  • kwired
    replied
    Originally posted by Russs57 View Post
    Couldn’t we run around the plant with an a amprobe and see which of the three phase conductors don’t sum to zero?

    Asking because I have limited experience in non standard systems.
    Maybe. If there is only one fault and it is (was) an ungrounded system there will be no "fault current" to cause a current imbalance on the supply conductors. This procedure will be more effective on a grounded system as that fault current will seek "ground".

    Leave a comment: