Hi,
After browsing this forum and the internet, it is unclear if the rounding rule of 220.5(B) can apply to PV calcs of section 690.8. However, here is my take on it:
1) NEC 220: applies to branch circuits, Feeder and Service calcs
2) NEC 220.5(B) allows us to round down for decimals <0.5A
3) NEC 220.3 asks us to check Table 220.3 for 'additions' or 'modifications' to article 220.
4) Table 220.3 tells us to refer to 690.8 (for 'additions' or 'modifications' of article 220)
5) NEC 690.8 says nothing about rounding up or down. All calcs have to be 'not less than 125%...'
CONCLUSION: 690.8 does not modify the rounding rules of 220.5(B) but adds safety factors to it. For example, if my total current is 20.125A I should be able to use a 20A breaker.
Does this sound OK to you guys? What is your experience on this matter?
Thanks!