studentofthecode
Member
- Location
- New Jersey
I have to set up a feeder that provides 250 to 600 amps for temporary connections of Emergency power for shutdown work. There are only 2 spare 400A breakers to supply this load. The main of the panel they are in is 1200 amp and can easily supply the current we need to use for our shutdowns. The wiring will be in identical lengths and terminated in a 800A power block in a j box.( What if it terminated in an 800A switch or C Breaker instead?)We are planning on running generator grade flexible cables to feed the gear temporarily. I'm thinking that the load will divide equally on the 500 Mcm phase conductors and will carry 1/2 of the load equally, according to Ohm's law. I know this is unorthodox, but it appears to work , in theory. I have not been able to find a code section that I can cite as a violation. Again, this is only for a temporary feeder that will be removed when repair work is complete. Thanks