Isc by utility companies

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi
do you know
why LADWP gives or reports available fault value sometimes more than 50000 amp
but SCE Edison utility company gives 4200 amp maximum

thank yiu
 

wbdvt

Senior Member
Location
Rutland, VT, USA
Occupation
Electrical Engineer, PE
Without more details, it could be that LADWP is giving a fault current based on an infinite bus and 50kA would be around a 2500kVA txf with a 480Y/277V secondary. SCE could be giving primary available fault current.

Really need more details.
 

kwired

Electron manager
Location
NE Nebraska
Less liability for them to give someone a high figure in this area than to give a figure that is low, especially if they didn't take the time to actually do the calculations specific to a particular installation.
 
Status
Not open for further replies.
Top