Fire alarm disconnects

Status
Not open for further replies.

Natfuelbilll

Senior Member
I have a single service supplying five remote buildings. Each building has a fire alarm panel. The engineer (AHJ) calls for installing a fire alarm switch on the line side of each building main.

Is the fire alarm panel fed by a service disconnect switches (service rules apply) or feeder tapped switches (tap rules apply)?

Service rules would let me install #8 wire. Feeder rules call for installing 500kcmil taps for the 3200A feeder breaker.

The load for each panel is 12A.

I'm looking to prepare my argument for #8.....
 

dkidd

Senior Member
Location
here
Occupation
PE
230.82(5) 2014.
But it won't pass as a required emergency power source, so why bother?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I have a single service supplying five remote buildings. Each building has a fire alarm panel. The engineer (AHJ) calls for installing a fire alarm switch on the line side of each building main.

Is the fire alarm panel fed by a service disconnect switches (service rules apply) or feeder tapped switches (tap rules apply)?

Service rules would let me install #8 wire. Feeder rules call for installing 500kcmil taps for the 3200A feeder breaker.

The load for each panel is 12A.

I'm looking to prepare my argument for #8.....

Are you installing in NYC or some other fruitcake jurisdiction that requires line-side taps for fire alarm systems? It is not a requirement of NFPA 72 or NFPA 70.
 