I have a single service supplying five remote buildings. Each building has a fire alarm panel. The engineer (AHJ) calls for installing a fire alarm switch on the line side of each building main.
Is the fire alarm panel fed by a service disconnect switches (service rules apply) or feeder tapped switches (tap rules apply)?
Service rules would let me install #8 wire. Feeder rules call for installing 500kcmil taps for the 3200A feeder breaker.
The load for each panel is 12A.
I'm looking to prepare my argument for #8.....