We got a plan review back from the AHJ where they noted to upsize the ground conductor where the ungrounded conductors are increased per 250.122(B). However, the phase conductors are larger due to ampacity adjustment and not due to voltage drop. (They were increased in size due to the circuit being 3-phase 4W 208 and considering the neutral as a CCC. Therefore we have 4CCC and derated by 80% based on the 90 degree column as opposed to the 75 degree column per 110.14(C).)
We noted that per the 2011 NEC handbook in the text below 250.122(B), it indicates the ground does not need to increase in size due to ampacity adjustment. "Increases in ungrounded circuit conductor size for the purposes of ampacity adjustment, correction, or both are not required to be considered in applying the provisions of 250.122(B)." However, the AHJ is using the 2008 NEC. Does similar language exist in the 2008 NEC? We were not able to locate it.
We are hoping we can simply indicate the conductors are larger due to ampacity adjustment which does not require upsizing the ground.
We then explained to the AHJ how we derated the conductors using the 90 degree column and referenced section 110.14(C). The AHJ noted you can't do that unless all the terminals etc are rated for 90 degree C. We then explained to the AHJ that if after applying the derating that the size we show is the first acceptable size conductor then we really didn't upsize.
Even if we wanted to upsize the ground proportionally to accommodate the AHJ, and we are starting with the first available conductor size based on 80% of 90 degree column (even though we are using the 75 degree terminations), what conductor would we then use as a starting point?
We noted that per the 2011 NEC handbook in the text below 250.122(B), it indicates the ground does not need to increase in size due to ampacity adjustment. "Increases in ungrounded circuit conductor size for the purposes of ampacity adjustment, correction, or both are not required to be considered in applying the provisions of 250.122(B)." However, the AHJ is using the 2008 NEC. Does similar language exist in the 2008 NEC? We were not able to locate it.
We are hoping we can simply indicate the conductors are larger due to ampacity adjustment which does not require upsizing the ground.
We then explained to the AHJ how we derated the conductors using the 90 degree column and referenced section 110.14(C). The AHJ noted you can't do that unless all the terminals etc are rated for 90 degree C. We then explained to the AHJ that if after applying the derating that the size we show is the first acceptable size conductor then we really didn't upsize.
Even if we wanted to upsize the ground proportionally to accommodate the AHJ, and we are starting with the first available conductor size based on 80% of 90 degree column (even though we are using the 75 degree terminations), what conductor would we then use as a starting point?