Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
So, here is my situation. I have a job spec that the panels are to be series rated. All well and good. However, the distribution goes from a Siemens main panel, through a UPS (equipped with bypass) then to another provided Siemens panel. Obviously when the system is in bypass it series rates with the up stream panel. My instinct says that a 15KVA UPS can't possibly have an AIC rating higher than 10K, but I can't find that information, or the impedance of the output circuit in the documentation. The documentation lists the SCCA at 30KA and the overload capacity as 150% of 41.6A via the battery or normal operation, and 800% for 500ms for bypass. Do I just assume that the KAIC can't be higher than 10K or is there something else that is my responsibility?
P.S. Speak slowly because I have resisted wrapping my head around a deep understanding of AIC calculations.
P.S. Speak slowly because I have resisted wrapping my head around a deep understanding of AIC calculations.