Hey all I have some questions on generator field forcing.
I am looking at a generator decrement curve and trying to determine if the field forcing effect is included in the decrement curve or not. As you can see, the curve levels out at about 1s at about 2.5PU.
Would the current theoretically just go to 0 if there is no field forcing? I've seen other decrement curves where the fault current dips down, and then increases again before it levels off in which I'm certain that is a result from field forcing. But when it just levels off without increasing again, is there still field forcing taking place? The generator includes a main output breaker in which I would like to set it to trip in its short time pickup region when it senses a fault. Field forcing affects where the STPU needs to be set in order to catch it.
The particular generator I'm looking at is a 1MW, 480V MTU permanent magnet engine generator.
I am looking at a generator decrement curve and trying to determine if the field forcing effect is included in the decrement curve or not. As you can see, the curve levels out at about 1s at about 2.5PU.
Would the current theoretically just go to 0 if there is no field forcing? I've seen other decrement curves where the fault current dips down, and then increases again before it levels off in which I'm certain that is a result from field forcing. But when it just levels off without increasing again, is there still field forcing taking place? The generator includes a main output breaker in which I would like to set it to trip in its short time pickup region when it senses a fault. Field forcing affects where the STPU needs to be set in order to catch it.
The particular generator I'm looking at is a 1MW, 480V MTU permanent magnet engine generator.