Mindrunnder88
Member
- Location
- Hilo, Hawaii, USA
Have a curious challenge with an idea for an interesting solution...
Have a site that is supported by a primary power source at the site (480Y/277V 3PH, 4w). We are intending to install another supply from a secondary power source that is about 4000' away. The typical load on the secondary will be well under 100A. However, certain instances (maybe for an hour or two a week) will result in this load jumping to a max of 200A. The cost of the secondary is our primary enemy, namely due to VD. Going to 600V using xfrms on each end, at 3% we would be looking at 3 sets of 500 for the run (over $350K for just the wire here).
Here's the idea that needs vetting. As the supported loads are primarily motors (and other inductive loads), we size to 7-10% VD (to stay within the voltage range of the motors), which would allow us to use one set of 500 instead of three. The motors will draw more current, but with the oversized wire, we won't even come close to ampacity limitations. The increased current will cause more VD, but it tapers off pretty quick. So all seems to check out.
Obviously, medium voltage would seem like a smart option for this situation, but there are specific reasons we are staying away from that.
Anybody see any issues with this (other than making sure we are seeing voltage at the equipment within range)?
Have a site that is supported by a primary power source at the site (480Y/277V 3PH, 4w). We are intending to install another supply from a secondary power source that is about 4000' away. The typical load on the secondary will be well under 100A. However, certain instances (maybe for an hour or two a week) will result in this load jumping to a max of 200A. The cost of the secondary is our primary enemy, namely due to VD. Going to 600V using xfrms on each end, at 3% we would be looking at 3 sets of 500 for the run (over $350K for just the wire here).
Here's the idea that needs vetting. As the supported loads are primarily motors (and other inductive loads), we size to 7-10% VD (to stay within the voltage range of the motors), which would allow us to use one set of 500 instead of three. The motors will draw more current, but with the oversized wire, we won't even come close to ampacity limitations. The increased current will cause more VD, but it tapers off pretty quick. So all seems to check out.
Obviously, medium voltage would seem like a smart option for this situation, but there are specific reasons we are staying away from that.
Anybody see any issues with this (other than making sure we are seeing voltage at the equipment within range)?