CADWELD & PGE
Open Neutral
Inside the Beltway
Engineer
I was working on a job in NoCal where we'd be fed 3-ph by PGE.
They required 2 grounds for the pad-mount transformer.
Their "Green Book" specified the type of clamp.
I wanted to CADWELD the wire to the rod. They didn't want to accept that and could not explain why.
I did "when in Rome" and clamped the wire AND then CADWELDed it too.
But I still wonder -- why wouldn't they want a welded connection?
rbalex
Mission Viejo, CA
Professional Electrical Engineer
Depending on the size of the conductor, Cadwelds may have internal voids/pits that can reduce the cross-sectional area of the connection and reduce its effective ampacity. The phenomena can begin around #4 AWG. Truthfully, this isn't generally a serious problem with grounding electrode connections but it can be a big deal with some bonding connections.
Fulthrotl
~Autocorrect is My Worst Enema.~
more and more, i've seen specifications that want a compression connection,
and they want to be able to see the die number witness on the fitting.
in other words, burndy 12 ton press, and burndy dies. not universal, which i think
is a bunch of hooey, but it's 'cause the harbor freight crimpers that are metric, and
don't get things stuck together well enough.
it's been almost 10 years since i did a cadweld.
Julius Right
Electrical Engineer Power Station Physical Design Retired
IEEE 142/2007 Green Book
4.3.3 Connecting to electrodes
Connections to electrodes are usually made by one of several means: mechanical, fusing,
or compression. The first of these methods, mechanical fittings, is best suited for making
connections to ground as the fittings are often easily disconnected, allowing for periodic
ground-to-earth measurements.
Open Neutral
Inside the Beltway
Engineer
My perspective is the biggest threat to a good ground is a corroded connection, 20 years after the fact. That's why I preferred welded connections.
I'm puzzled that the standards folks are seemingly unconcerned about that.
tortuga
Code Historian
Oregon
Electrical Design
Easily disconnected, allowing for periodic
ground-to-earth measurements[
:thumbsup: