  • myspark
    replied
    Originally posted by Mark1990 View Post
    A little more detail on the machine. The prints call out several options not installed, totaling 33hp. Motors that are utilized are 27.5 kw servo and a 7.2 kw servo, along with a 7.5 kva transformer, for some 120 v loads. Maybe the nameplate includes the never installed options? My main question is, does the code allow me to run a smaller feed than the nameplate calls for? I dont see this anywhere in article 670. Any help is appreciated . Thank you
    This comment is based on your (purported) details notwithstanding other details you provided (eg) 192 FLA etc.
    The 33 HP name plate does make sense for existing #10 wiring

    I surmise this is a press trim guillotine type cutter?
    Most of this type machines are based on the GENEVA mechanism (i.e.) only one motor is running all the time while other motors that comprise the whole unit like indexing servos--only operate when called for. And when they do--they only operate momentarily.
    Typical machines found in book binding and CNC machines.

    Using the as-built info would resolve your dilemma.

    (Touring the Biomass Generating Plant in Norway)

    Leave a comment:


  • Besoeker3
    replied
    Originally posted by electrofelon View Post
    Got a letter/number punch set with a "." in it
    Maybe nail on head ?

    Leave a comment:


  • retirede
    replied
    Originally posted by jim dungar View Post
    I don't see a problem.

    NEC 2017
    670.3(A)(2) - nameplate must list the maximum possible overcurrent protective device.
    670.4(A) - The conductor sizing shall take into account the loads that will be connected at one time based on their duty cycle.670.4(C) the overcurrent device is sized to handle the full load current connected at one time.
    And since it ran for 8 years without problems on a 30A ocpd, it will obviously handle the actual full load current.

    Leave a comment:


  • jim dungar
    replied
    Originally posted by Mark1990 View Post
    As everything I read in the code points to sizing the conductors and over current protection based on machine nameplate FLA.
    I don't see a problem.

    NEC 2017
    670.3(A)(2) - nameplate must list the maximum possible overcurrent protective device.
    670.4(A) - The conductor sizing shall take into account the loads that will be connected at one time based on their duty cycle.670.4(C) the overcurrent device is sized to handle the full load current connected at one time.

    Leave a comment:


  • electrofelon
    replied
    Originally posted by MrJLH View Post
    Maybe the poster meant 19.2 amps?
    Originally posted by Mark1990 View Post
    I agree that practically speaking as long as conductors are properly protected there is not a fire hazard etc. my main sticking point is if the job were to be audited by our fire insurance company or corporate for some reason I would like a code to reference that allowed a smaller than nameplate service. As everything I read in the code points to sizing the conductors and over current protection based on machine nameplate FLA.
    Got a letter/number punch set with a "." in it

    Leave a comment:


  • Mark1990
    replied
    I agree that practically speaking as long as conductors are properly protected there is not a fire hazard etc. my main sticking point is if the job were to be audited by our fire insurance company or corporate for some reason I would like a code to reference that allowed a smaller than nameplate service. As everything I read in the code points to sizing the conductors and over current protection based on machine nameplate FLA.

    Leave a comment:


  • LarryFine
    replied
    With the history of operation you provided, I would just duplicate what you have, and sleep well.

    Leave a comment:


  • retirede
    replied
    Sizing loads to industrial machinery

    I think if the conductors are properly protected, you’re fine code-wise.

    I have had similar experiences. We had machine tools that were never loaded anywhere near capacity. A vertical turret lathe with an integral 100 A breaker that never drew more than 15A the way it was used. Not uncommon.

    We never downsized the conductors, however. We never knew what kind of work it would be asked to do next month!

    Leave a comment:


  • Mark1990
    replied
    A little more detail on the machine. The prints call out several options not installed, totaling 33hp. Motors that are utilized are 27.5 kw servo and a 7.2 kw servo, along with a 7.5 kva transformer, for some 120 v loads. Maybe the nameplate includes the never installed options? My main question is, does the code allow me to run a smaller feed than the nameplate calls for? I dont see this anywhere in article 670. Any help is appreciated . Thank you

    Leave a comment:


  • MrJLH
    replied
    Originally posted by Mark1990 View Post
    We have in our factory a trim press machine with a nameplate FLA of 192 amps at 460 v 3 phase. No resistive load, just a control plc and 2 servo motors. Avg draw using a clamp on meter is 10 to 15 amps. It is fed from a 30 amp breaker with #10 wire and we have not had any problems for the 8 years this machine has been running, 3 shifts , five days a week. I need to relocate this machine within our factory. I’m stumped at finding a code allowace for under sizing a load, even though experience shows 30amps is more than enough. I hate to install a 200 amp service unnecessarily,but i dont want to be violating any codes at the same time. Any help would be greatly appreciated.
    Maybe the poster meant 19.2 amps?

    Leave a comment:


  • Dennis Alwon
    replied
    I don't believe the nameplate is correct. What is the HP of the motor?

    Leave a comment:


  • Mark1990
    started a topic Sizing loads to industrial machinery

    Sizing loads to industrial machinery

    We have in our factory a trim press machine with a nameplate FLA of 192 amps at 460 v 3 phase. No resistive load, just a control plc and 2 servo motors. Avg draw using a clamp on meter is 10 to 15 amps. It is fed from a 30 amp breaker with #10 wire and we have not had any problems for the 8 years this machine has been running, 3 shifts , five days a week. I need to relocate this machine within our factory. I’m stumped at finding a code allowace for under sizing a load, even though experience shows 30amps is more than enough. I hate to install a 200 amp service unnecessarily,but i dont want to be violating any codes at the same time. Any help would be greatly appreciated.