wireway fill
mannyb
Florida
I need to a wireway for 6 paralleled 4-600mcm looking to see if i did this right. I wanted to use a 12x12 wireway
12x12x20%= 28.8 / .8676 or 600mcm wire= 33.1 meaning i can install 33-600mcm wires. So i can use 12x12 wireway? did i do this right?
oldsparky52
Looks right to me.
I'm assuming you are not going to splice in this wireway.
mannyb
Florida
Looks right to me.
no Sir we just need the wireway to extend wire into building. We want to use wireway as a chase or extention into a Switchboard. BTW You think we need to use bonding bushings to each and or all penetrations?? There will be 6 conduits for feed.
oldsparky52
If you are punching your own holes to the correct size, then no you don't need a bonding bushing. I would however use a bonding locknut (that's just me).
What type conduit are you using?
Where are you entering the wireway (at the ends only, at the top or bottom, or combination)?
Designer69
do electricians typically use power distribution blocks inside wireways or do they prefer to just splice the cables?