    Transformer Primary Conductors Calculation

    Hey Guys,

    We have a Solar system installed with the following specs:
    - Voltage: 480 V
    - Current: 1080 A

    This is fed into the secondary of the 1000 kVA transformer with 4kV on the primary whose spec. is:
    kVA= (1.732 x 480 x 1080)/1000 = 897.895 kVA (1000 kVA is used)

    From this the primary current will be:
    I = 897.995*1000/1.732*4000 = 129.6 A

    The POCO asked us to use a 2/0 wire for the primary, but I wanted to verify this so, Can someone please provide a step by step process to calculate the conductor size for the primary according to NEC?

    Thanks in Advance

    #2
    Are you taking service at primary voltage? Where does does the 4kv go? Where is the service disconnect? Those answers will help.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

    Comment


      #3
      Originally posted by electrofelon View Post
      Are you taking service at primary voltage? Where does does the 4kv go? Where is the service disconnect? Those answers will help.
      The 4kV is directly connected to the grid which is the service voltage from the POCO, this is an underground run. Hope this helps. Please check attached
      Click image for larger version

Name:	1.jpg
Views:	1
Size:	17.4 KB
ID:	2380805
      Last edited by TheElectrician; 05-23-19, 02:52 PM.

      Comment


        #4
        Where is the service disconnect?
        Ethan Brush - East West Electric. NY, WA. MA

        "You can't generalize"

        Comment


          #5
          Originally posted by electrofelon View Post
          Where is the service disconnect?
          Do you mean the primary protection of the transformer? if so it is not added in this one line, but there is a disconnect before (on the secondary side) of the transformer.
          Last edited by TheElectrician; 05-23-19, 05:28 PM.

          Comment


            #6
            Did you ask the PoCo rep why they are requiring this size conductor?

            What size conductor do you want to install, and what table would you use for its ampacity rating?
            Last edited by oldsparky52; 05-24-19, 07:04 AM.

            Comment


              #7
              Originally posted by TheElectrician View Post

              The POCO asked us to use a 2/0 wire for the primary,

              Thanks in Advance
              Once you provide it, it becomes their property and they would maintain it as the 1000 KVA transformer is theirs and so not covered by NEC. Isn't it?

              Comment


                #8
                Originally posted by Sahib View Post
                Once you provide it, it becomes their property and they would maintain it as the 1000 KVA transformer is theirs and so not covered by NEC. Isn't it?
                My thought too.
                Perhaps not the owning but the specifying as to being a feeder into primary power.

                Comment


                  #9
                  Originally posted by oldsparky52 View Post
                  Did you ask the PoCo rep why they are requiring this size conductor?

                  What size conductor do you want to install, and what table would you use for its ampacity rating?
                  Yes, I asked the power company, they just asked me to follow their spec sheet and didnt give any further information on how they came up with it. They just are not giving that information. I was using the the teriplex conductor table 310.60(74) AL for 15kV, for sizing it using the derate factor 1.25

                  Comment


                    #10
                    Originally posted by Sahib View Post
                    Once you provide it, it becomes their property and they would maintain it as the 1000 KVA transformer is theirs and so not covered by NEC. Isn't it?
                    You are right, although they provided the t/f the customer owns it, but still they wanted to install the conductor by their specs, and I wanted to figure out how they came up with that number.

                    Comment


                      #11
                      Originally posted by TheElectrician View Post
                      Yes, I asked the power company, they just asked me to follow their spec sheet and didnt give any further information on how they came up with it. They just are not giving that information.
                      Do you think they may be calculating the 1,000KVA transformer at 100% usage instead of using the input amperage like you were? I calculate that to be 144.3-amps.




                      I was using the the teriplex conductor table 310.60(74) AL for 15kV, for sizing it using the derate factor 1.25
                      I never did any of this work so please excuse my ignorance, but what is the 1.25 factor for? Temperature, ...? You are multiplying the table ampacity by 1.25 to come up with the allowed ampacity?

                      W/out any adjustments, it would take a 2/0 cable to meet or exceed (using the table you mentioned) that 144-amp calculation.

                      I'm just speculating.

                      Comment


                        #12
                        Originally posted by TheElectrician View Post
                        Do you mean the primary protection of the transformer? if so it is not added in this one line, but there is a disconnect before (on the secondary side) of the transformer.
                        No, I mean the service disconnect, but the service disconnect and the primary protection could be the same
                        Ethan Brush - East West Electric. NY, WA. MA

                        "You can't generalize"

                        Comment


                          #13
                          Originally posted by oldsparky52 View Post
                          Do you think they may be calculating the 1,000KVA transformer at 100% usage instead of using the input amperage like you were? I calculate that to be 144.3-amps.
                          Yes, I think so too. But is that the right way to do it? I assume we have to take the load current here which is 1080A, using that I get the primary current to be 129.6A. So should we take the name plate detail (1000kVA) to calculate the primary or the kVA (897.89 kVA) calculated from the load current (1080A)?

                          Originally posted by oldsparky52 View Post
                          I never did any of this work so please excuse my ignorance, but what is the 1.25 factor for? Temperature, ...? You are multiplying the table ampacity by 1.25 to come up with the allowed ampacity?

                          W/out any adjustments, it would take a 2/0 cable to meet or exceed (using the table you mentioned) that 144-amp calculation.

                          I'm just speculating.
                          That is alright this is the first time I am designing medium voltage so I might be missing something here too. I thought I have to use the 1.25 factor which is mentioned in the Step 3 in the following link: https://www.mikeholt.com/mojonewsarc...n~20020516.htm

                          So from this 144A*1.25=180A, cross referencing this with the table 310.60(C)(74) AL, I came up with the 2/0

                          But do let me know if that is the right way to do it from your experience. Thanks

                          Comment


                            #14
                            Originally posted by electrofelon View Post
                            No, I mean the service disconnect, but the service disconnect and the primary protection could be the same
                            Yes, initially we didnt have a primary protection for the transformer, then we added it later. But on the same topic, Do I have to have a primary protection for the transformer like a service disconnect designed using the table 430.30 even if I connect the primary of the transformer directly to 4kV line of the utility via manhole?

                            Comment


                              #15
                              Originally posted by TheElectrician View Post
                              Thank you for that, I should have known that. duh

                              Comment