Two questions.
1.Have a 120/208v 400A fused switch feeding sprinkler booster pump controller( the pump is 30HP) with 3#2 & 1#3 MU cable. According to Pyrotenax website(for the MI) and 310.17 #2 is only good for between 100A-150A 75 degree. Doesn’t the feeder(MI) need to be sized to the 400A switch.
2. See attached pic. Showing a bus tap from the 4000a board feeding another 400A bus. Isn’t a OCPD required? Also, this feeder should be sized to the 4000A bus, correct? Thanks.
1.Have a 120/208v 400A fused switch feeding sprinkler booster pump controller( the pump is 30HP) with 3#2 & 1#3 MU cable. According to Pyrotenax website(for the MI) and 310.17 #2 is only good for between 100A-150A 75 degree. Doesn’t the feeder(MI) need to be sized to the 400A switch.
2. See attached pic. Showing a bus tap from the 4000a board feeding another 400A bus. Isn’t a OCPD required? Also, this feeder should be sized to the 4000A bus, correct? Thanks.