NEC 2017, How is Table 220.88 Optional Method applied to a load calculation in a new all electric restaurant, and just to use as an example if the total connected load would be 326-800A ?
For Table 220.88 the connected load is kVA, not Amps.
If you had a 600kVA connected load in an all electric restaurant, the 220.88 calculated load would be (600-325)*0.45+262.5 or 386.3kVA