    NEC 2017, How is Table 220.88 Optional Method applied to a load calculation in a new all electric restaurant, and just to use as an example if the total connected load would be 326-800A ?

    #2
    Originally posted by juanbtrevino1@yahoo.com View Post
    NEC 2017, How is Table 220.88 Optional Method applied to a load calculation in a new all electric restaurant, and just to use as an example if the total connected load would be [COLOR=#ff0000]326-800A[/COLOR] ?
    For Table 220.88 the connected load is kVA, not Amps.

    If you had a 600kVA connected load in an all electric restaurant, the 220.88 calculated load would be (600-325)*0.45+262.5 or 386.3kVA