    #91
    Circuit switcher should have been in place and functioning at the time of the event:
    Attached Files
    Our comedian shamelessly joked about a blackout. Talk about dark humor.

    Comment


      #92
      Originally posted by mbrooke View Post
      Circuit switcher should have been in place and functioning at the time of the event:
      Are those maintenance outages TBA....?

      ~RJ~

      Comment


        #93
        Originally posted by romex jockey View Post
        Are those maintenance outages TBA....?

        ~RJ~
        Yes- they must be scheduled ahead of time. Perhaps they were never approved now that you ask. But I am inclined to doubt it.
        Our comedian shamelessly joked about a blackout. Talk about dark humor.

        Comment


          #94
          FWIW, looking at other stations listed as "Beyond 2018" seem to have been equipped with a circuit switcher in the past year.



          Bruckner:
          Attached Files
          Our comedian shamelessly joked about a blackout. Talk about dark humor.

          Comment


            #95
            Other side of Bruckner:
            Attached Files
            Our comedian shamelessly joked about a blackout. Talk about dark humor.

            Comment


              #96
              Hell Gate:
              Attached Files
              Our comedian shamelessly joked about a blackout. Talk about dark humor.

              Comment


                #97
                Jamaica:
                Attached Files
                Our comedian shamelessly joked about a blackout. Talk about dark humor.

                Comment


                  #98
                  Approximate single line breaker diagram of West 65st:
                  Attached Files
                  Our comedian shamelessly joked about a blackout. Talk about dark humor.

                  Comment


                    #99
                    Drawing ended up being big so I had to shrink it and split it into two.
                    Attached Files
                    Our comedian shamelessly joked about a blackout. Talk about dark humor.

                    Comment


                      If anyone is curious is how MV is typically distributed and used in a network.


                      Small buildings are directly fed from the 208 volt mesh where as large buildings take 4 or more 13.8kv cables and have spot networks inside the building. Typically roughly every 10 floors will require a spot network- not uncommon for Manhattan buildings to have one or two in the basement, one or two on the middle mechanical equipment room and one or two on the roof.


                      Again the loss of two 13.8kv cables should not trigger equipment over load or an outage- even 3 cables is usually no issue outside of high load periods. Loss of 3 or 4 13.8kv cables supplying the 208 volt street mesh is typically not a problem outside the most hottest days.


                      Typically the secondary 208 volt cables are 500MCM phase and 4/0 neutral.
                      Attached Files
                      Our comedian shamelessly joked about a blackout. Talk about dark humor.

                      Comment