    We won a job just recently and the ATS's were 175A and now reduced to 125A via change order. They just got the order last week. I'm confused by the email the ATS vendor sent out saying no credit due to the size reduction. The client is expecting a credit and I would think going down to 125A would result in the ATS's being cheaper. Below is the response. Doesn't make sense to me.

    The rating changes for the (3) ATSs is not going to impact the PO pricing since we already upsized all ATSs to accommodate the 65kAIC specific breaker WCR.

    #2
    Makes no sense to me.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

    Comment


      #3
      Originally posted by infinity View Post
      Makes no sense to me.
      I assume you mean the response from the vendor, correct?

      Comment


        #4
        Originally posted by mstrlucky74 View Post
        I assume you mean the response from the vendor, correct?
        Yes.
        Rob

        Moderator

        All responses based on the 2014 NEC unless otherwise noted

        Comment


          #5
          It sounds like they're saying that they gave you a short-circuit-interrupting rating upgrade without charge, and are now recouping the cost of their mistake.
          Master Electrician
          Electrical Contractor
          Richmond, VA

          Comment


            #6
            Im not an expert on those especially ordering them but 50a difference IMO shouldn't reflect a huge price difference anyone agree?

            Sent from my SM-G965U using Tapatalk

            Comment


              #7
              Originally posted by mstrlucky74 View Post
              We won a job just recently and the ATS's were 175A and now reduced to 125A via change order. They just got the order last week. I'm confused by the email the ATS vendor sent out saying no credit due to the size reduction. The client is expecting a credit and I would think going down to 125A would result in the ATS's being cheaper. Below is the response. Doesn't make sense to me.

              The rating changes for the (3) ATSs is not going to impact the PO pricing since we already upsized all ATSs to accommodate the 65kAIC specific breaker WCR.
              Just a guess - they priced you something with 175A breaker with high interrupt rating, now you are asking for 125A same high interrupt rating. To get same interrupt rating they may still need to use same frame size/type of breaker and maybe even other components of the assembly are same thing and cost of that doesn't really change.
              I live for today, I'm just a day behind.

              Comment


                #8
                Originally posted by kwired View Post
                Just a guess - they priced you something with 175A breaker with high interrupt rating, now you are asking for 125A same high interrupt rating. To get same interrupt rating they may still need to use same frame size/type of breaker and maybe even other components of the assembly are same thing and cost of that doesn't really change.
                Thanks. So when you says interrupting rating you mean AIC?

                Comment


                  #9
                  Originally posted by mstrlucky74 View Post
                  Thanks. So when you says interrupting rating you mean AIC?
                  yes
                  I live for today, I'm just a day behind.

                  Comment


                    #10
                    ATS's are typically either rated for 100A or 200A. (The 200A might actually be a 225A or a 250A depending on the brand.)

                    So I wouldn't expect any change in price unless you reduce it to 100 amps. (Edit: Both the 125A and 175A spec are going to require the same 200A ATS.)

                    And with the 65KAIC specific breaker rating may also prevent them from reducing the ATS size.

                    So I'm not surprised you aren't getting any savings.

                    Comment


                      #11
                      If the spec required a 65kA short circuit rating, they upsized the ATS to accommodate the rating to work with the specific withstand current rating (WCR) and now that you want to reduce the ampacity, it still doesn't change the switch size if you don't reduce the 65kA WCR requirement.

                      There will be a savings on your wire though.
                      Ron