Feeder run under pool
PE (always learning)
Saint Louis
Professional Engineer
Hey everyone,
Just curious, but is there anything in the NEC that prohibits running feeders under a pool? The pool is located in the basement of a hotel and the feeder would run underground. Let me know what you think.
Best Regards,
Engineer In Training
WA_Sparky
Electrical Engineer
Vancouver, WA, Clark
Electrical Engineer
Check out the Code book
680.11: Underground wiring shall not be permitted under the pool unless this wiring is necessary to supply pool equipment permitted by this article. Min cover depths need to comply with 300.5
infinity
New Jersey
Journeyman Electrician
Not only can it not go under the pool it needs to also be a minimum of 5' from the edge of the pool.
packersparky
Wisconsin
Inspector
Not if your area is under the 2017 NEC. That section has been revised.
From the 2014 NEC:
680.10 Underground Wiring Location. Underground
wiring shall not be permitted under the pool or within the
area extending 1.5 m (5 ft) horizontally from the inside
wall of the pool unless this wiring is necessary to supply
pool equipment permitted by this article. Where space limitations
prevent wiring from being routed a distance 1.5 m
(5 ft) or more from the pool, such wiring shall be permitted
where installed in complete raceway systems of rigid metal
conduit, intermediate metal conduit, or a nonmetallic raceway
system. All metal conduit shall be corrosion resistant
and suitable for the location. The minimum cover depth
shall be as given in Table 680.10.
From the 2017 NEC:
680.11 Underground Wiring Location. Underground wiring
shall be permitted where installed in rigid metal conduit, intermediate
metal conduit, rigid polyvinyl chloride conduit, reinforced
thermosetting resin conduit, or Type MC cable, suitable
for the conditions subject to that location. Underground wiring
Minimum cover depths shall be as given in Table 300.5 .
infinity
New Jersey
From the 2014 NEC:
From the 2017 NEC:
We're still under the 2014 but it does make sense to get rid of the 5' limitation because the 5' rule seemed to be completely arbitrary.