Re: Oil insulated cable
"Oil-o-static" is a trade name used by Okonite Cables, NJ.  This type of cable is genericly called "pipe type cable" and normally used only at 69kV and above.  It is basically three paper insulated cables in a steel pipe pressurized with a "dielectric fluid" to about 200 psi.  This is mainly a system used in the USA and the Americas for HV and EHV utility power transmission up to 345kV.
 Oil filled cable also called "hollow core cable" or "Pirelli cable" has as the name implies a hollow conductor used as a fluid supply channel to pressurize the cable.  These cables have been used in the US at 35kV and above but are used a lot overseas possibly as low as 15kV and up to 230kV for bulk power transmission.  These operate at pressures ranging from 15 to 200 psi.
 PILC or "Paper Lead Cable", (also called "solid cable"), is an oil impregnated paper insulation that has an outer jacket of lead and usually some plastic over that, on the newer ones anyway.  There is no pressurizing source for the oil so it operates at atmospheric pressure. This type has been used all over the world at 5 to 35kV since shortly after Thomas Edison did his thing.  I have seen samples from as early as around 1910.
 Terminating and splicing PILC usually requires solder wiping the accessory to the lead jacket of the cable to form the outer seal.  While terminating and splicing EPR is done by hand taping, heat shrinking  or cold shrinking (zipper) methods.
 You can join EPR to PILC by building a suitable oil barrier on the PILC cable end, so the oil doesn't bleed into the EPR.  There are special splice kits available for this.  Our you can build two terminals and attach them through a bus.  Depends if you are in a manhole, ditch or on a pole.
 Good Luck!
 EHV Mark