Re: 3-Phase Delta Currents:
tjester,
Only 2 loads. If we label the three phases A, B, & C, then I disconnect one of the secondaries, say AB, and let us call this isolated secondary A'B'. Then I connect a load, 2R, across A'B', and I connect a second load, 2R, across AB. Line C is not connected. Since Va'-Vb' = Va - Vb in magnitude and phase, the currents in the two loads will be equal in magnitude and phase. Then if I connect A to A' and B to B', the load is now R, and the windings AC and CB act as one to provide half the current, and the winding AB provides the other half.
Since this is an IDEAL xfmr, no resistance, no leakage reactance, no iron loss, there is nothing to impede the current. As I say, you cannot prove this in the lab because such xfrmrs are not available. The 1/3, 2/3 rule of thumb applies to real xfrmrs, not ideal xfrmrs.