Re: DC Distribution Standard
Standards and specifications are not going to be found in the NEC. As Wayne said if it is calss 1, 2, or 3 minimum requirements are found in 725, otherwise all other articles apply.
One word of warning if you are working with low voltage dc say like 12, 24, or 48 the cable sizes listed in 310.16 may not work because they are not based on voltage drop, only current. Low voltage dc cannot tolerate very much voltage drop. Typically a 12 volt system voltage drop is 1/2 volt, 24 @ 1 volt, and 48 @ 2 volts. Same can be said of article 250.122 the cable sizes listed may not be able to induce enough fault current to operate protection devices.