Trying to remember where this 2017 added requirement is for signage indicating status of N-G bonding at the generator? Does someone know off the top of their head?
Thanks,
Mike
infinity
New Jersey
Journeyman Electrician
Also look at 702.7(C):
702.7(C) Power Inlet. Where a power inlet is used for a tem-
porary connection to a portable generator, a warning sign
shall be placed near the inlet to indicate the type of derived
system that the system is capable of based on the wiring of
the transfer equipment. The sign shall display one of the
following warnings:
WARNING:
FOR CONNECTION OF A SEPARATELY DERIVED
(BONDED NEUTRAL) SYSTEM ONLY
or
WARNING:
FOR CONNECTION OF A NONSEPARATELY
DERIVED (FLOATING NEUTRAL) SYSTEM ONLY