    ATS control from external source such as PLC

    Do any auto transfer switch experts her know if it's possible to control an ATS from an external signal?

    E.g., can I block/prevent a transfer if an external signal (say from a PLC) is present/wired to the ATS controller?


    I'm asking because they are requesting some more complex than usual control schemes using multiple ATS's/ interlocking etc.
    Thanks

    #2
    Is the transfer required to be completed with in a specific time frame, such as 700.12?
    Just because you can, doesn't mean you should.

    Comment


      #3
      You can invoke a transfer inhibit signal from a PLC for 701 and 702 loads
      Ron

      Comment


        #4
        Originally posted by ron View Post
        You can invoke a transfer inhibit signal from a PLC for 701 and 702 loads
        Thanks . So most ATS's typically have this feature? "transfer inhibit"

        Comment


          #5
          Originally posted by designer82 View Post

          Thanks . So most ATS's typically have this feature? "transfer inhibit"
          All the ones I've dealt with have it, but I have only worked with large ASCO and Russelectric units.
          Ron

          Comment


            #6
            Originally posted by designer82 View Post

            Thanks . So most ATS's typically have this feature? "transfer inhibit"
            Most commercial/industrial rated switches will have this natively or be available as an option. As others have indicated, if this ATS is for Article 700 load(s) this would not be allowed.

            Comment


              #7
              Originally posted by texie View Post

              Most commercial/industrial rated switches will have this natively or be available as an option. As others have indicated, if this ATS is for Article 700 load(s) this would not be allowed.
              Agree. I have done a previous install which the client asked to redo when the ATS transferred to emergency power in 42 seconds!

              Comment


                #8
                As others have stated, this is a common accessory/ option provided by all manufacturers on the newer microprocessor controllers. The cut-sheet GE 50R-2016 R15D_Q3 acc.pdf is attached that shows the R15 load shed and Q3 transfer inhibit options for the GE-Zenith ATS.
                If this feature is required on the older ATS units with relay logic then a simple circuit can be added using an interposing relay to prevent transfer to emergency.
                Ifyoucan'texplain itsimply youdon'tunderrstanditwellenough- Albert Einstein