When they tap a 3PH starter or circuit breaker for control power transformers or any other transformer for auxiliary loads, how do they actually make the bus tap? with a multi lug connector bolted to the bus?
Jraef
Moderator, OTD
Electrical Engineer
Depends on a number of things. If there is bus bar after the breaker you can drill and tap it. If it is wire, you can use splitter blocks, or get some breaker lugs with listed tap-off screws on them. Some starters have tap points on the line lugs. Lots of different ways to skin that cat.
designer82
Boston
I'm trying to tap this starter like shown. Have you seen this done? Maybe there's issues against doing this
I could even tap it ahead of the breaker and add another breaker, it doesn't matter.
Jraef
Moderator, OTD
Electrical Engineer
Almost all combination starters are done that way. usually the tap is done on the line side of the starter (contactor) because they generally have lugs on them for doing this. 4160V though, that's a different story. Assuming that's a Draw-Out breaker, it likely has tap lugs available for the breaker terminals.
designer82
Boston
Thank you
That auxiliary tap would be a 75KVA transformer though with #1/0 conductors. Wouldn't be for control voltage, it would be for a pump motor for a chiller chilled water pump.
kwired
Electron manager
NE Nebraska
Thank you
75kVA is just a little larger than the average control power transformer usually is:D