    Originally posted by winnie View Post
    The output of a small transformer with 480V applied to the 120V side would be smoke

    Seriously: the 4:1 ratio starts to fall apart as the core gets saturated. You see more leakage flux and mutual coupling from primary to secondary, so the voltage ratio changes. On top of this the saturation of the core means more magnetizing current flows and there is more voltage drop in the primary. I would expect a short duration transient (until something fails or OCPD opens) with rather less than a 4:1 ratio.

    -Jon
    We used wire up similar in the shop just to watch them blow up......
    Excellent comment Winnie
    Hahahaha
    Microwave Poison will be seen to be a Trillion times worse than Asbestos.

    Comment


      #17
      It still works. No smoke.
      Attached Files
      Tom
      TBLO

      Comment


        #18
        Originally posted by kwired View Post

        He already tried it, unintentionally, topic of another thread. It blew primary fuses immediately. After figuring out the problem and correcting it it still worked. An item connected to the secondary did fail though.
        The inrush saved him.