Anything wrong with doing this? Transf. connections

Status
Not open for further replies.

designer82

Senior Member
Location
Boston
Need to run 4160v to a load and and also step down to other loads as shown.

Does this look ok, any issues with it?

Thanks
 

Attachments

  • transf question.png
    transf question.png
    44 KB · Views: 0

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
As long as the breaker upstream on the 4160V side is sized to protect the wires serving the transformer primary and the wires serving the 4160V load, I think this is OK. I don't like it that much, however. In order to turn off one item, you need to turn off both.
 