Announcement
Collapse
No announcement yet.
Isolation Transformer
Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts
    I Just want to know that, Do we need isolation transformer for Computer loads and its associated Data/server racks.
    My previous experience say no we don't need it for computer load.
    I am on a hospital project where we are proposing Isolation transformer for ICU, ORs and medical equipment but my peer reviewer is of the view that we need isolation transformer for Data/computers load also.
    Any help in this regard is highly appreciated
    [COLOR=#ff0000]If you don't know, ask those who knows[/COLOR]
    #2
    I've not come across one required for that application. And I don't see why one would.
    Comment
      #3
      There could be a good reason to do it, but it is not a code requirement.
      Bob
      Comment
        #4
        Not sure that the NEC applies where Sajid is from..........
        Comment
          #5
          Questions...
          How stable and predictable is your power source and the associated grounding and bonding practices?
          do you have surges or spikes that would cause the data center to be damaged?
          why are you doing it for the other equipment?
          Using UPS? Will the associated harmonics going back to the mains be a problem?
          Comment
            #6
            NEC is not applied here but i need a general openion
            Comment
              #7
              Originally posted by Hv&Lv View Post
              Questions...
              Power source is not much stable as we have backup generators
              Yes we have a problem of surges and spikes during lightning and switching on and off of mechanical equipments
              Other equipment comprise of ORs and ICus equipment which are sensitive to harmonics and isolation transformers usually required for such applications
              Yes UPS harmonics in the mains is a problem..
              Comment
                #8
                That kind of answers your question.
                I would definitely put the isolation transformer in.
                Comment
                  #9
                  I think that harmonic mitigating transformers would be a more appropriate choice.
                  https://www.hammondpowersolutions.co...ng-transformer
                  The more they overthink the plumbing, the easier it is to stop up the drain
                  Comment
                    #10
                    An isolation transformer is not a fix for those issues.
                    Comment
                      #11
                      191010-1101 EDT
                      What is an isolation transformer? That needs to be defined.
                      I would not classify an ordinary transformer as an isolation transformer. It does provide DC isolation, and it does more or less remove common mode noise, but does not remove normal mode noise. See
                      https://micro.rohm.com/en/techweb/kn.../01-s-emc/6899
                      Nor does an ordinary transformer prevent capacitive coupling from primary to secondary.
                      Generally I would expect the definition of an isolation transformer as having an electrostatic shield added to an ordinary transformer.
                      Will an isolation transformer solve all the different problems Sajid has? No.
                      So the real question is what are the real problems?
                      Short time voltage drop out, a few cycles, could be very important. This will require a motor generator with lots of inertia, or an electronic UPS.
                      High voltage spikes can probably be reduced with voltage clampers (MOVs and other devices).
                      High frequency noise will require filters.
                      Internal problems like differential ground path noise require some sort of isolation, or using differential signaling circuits.
                      Comment
                        #12
                        Originally posted by gar View Post
                        191010-1101 EDT
                        Um......one where the primary and secondary are not electrically connected?
                        Comment
                          #13
                          191010-1101 EDT
                          Yes By isolation transformer i mean the transformer with electrostatic shielding that will be used to suppress harmonics.
                          Comment
                            #14
                            It won't suppress harmonics.
                            You need a filter for that.
                            Comment
                              #15
                              http://www.isca.in/IJES/Archive/v6/i...S-2017-053.pdf