    Do I need to bond the meter/disconnect panel? I looked on the diagram inside the panel and I didn't see where bonding should go.
    gusco

    #2
    Originally posted by guschash View Post
    Do I need to bond the meter/disconnect panel? I looked on the diagram inside the panel and I didn't see where bonding should go.
    Depending on the type wouldn’t the #6 to the ground rod attachment be the bond?

    Comment


      #3
      Originally posted by guschash View Post
      Do I need to bond the meter/disconnect panel? I looked on the diagram inside the panel and I didn't see where bonding should go.
      I think you are referring to a meter/maim combo. If that is the case all meter mains that I am aware of are listed "suitable for use ONLY as service equipment". The translation for that marking is it is factory bonded and can't be removed. This is different than equipment marked "suitable for use as service equipment" (SUSE) which would include a screw or jumper to be installed if required.
      That is why you don't see a screw or jumper to be installed.

      Comment


        #4
        If the meter/main is the service disconnect then your GEC(s) will terminate there on the neutral.
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted

        Comment


          #5
          Originally posted by Hv&Lv View Post

          Depending on the type wouldn’t the #6 to the ground rod attachment be the bond?
          Originally posted by infinity View Post
          If the meter/main is the service disconnect then your GEC(s) will terminate there on the neutral.
          Perhaps some confusion about what the OP means by "bond". To me, that means the main bonding jumper connecting the case/EGC bus to the grounded conductor, as Texie mentioned. I guess it could mean the GEC connection to the grounded conductor also.
          Ethan Brush - East West Electric. NY, WA. MA

          "You can't generalize"

          Comment


            #6
            Originally posted by electrofelon View Post



            Perhaps some confusion about what the OP means by "bond". To me, that means the main bonding jumper connecting the case/EGC bus to the grounded conductor, as Texie mentioned. I guess it could mean the GEC connection to the grounded conductor also.
            Could be.
            Rob

            Moderator

            All responses based on the 2017 NEC unless otherwise noted

            Comment


              #7
              Thanks everyone . I thought that it might be factory bonded but wasn't sure. Yes Infinity that's what I am asking. Connecting the case/EGC to the grounded conductor.