For a detached garage with one lighting circuit would you need to provide a disconnect? I thought you only needed a disconnect for more than one circuit is that correct?
kjw444 said:For a detached garage with one lighting circuit would you need to provide a disconnect? I thought you only needed a disconnect for more than one circuit is that correct?
kjw444 said:Thanks for clearing everything up. Now days around here its sort of odd to have a detached garage for new construction.
stickboy1375 said:This rule goes for ANY outbuilding, not just a garage...
infinity said:Actually it is required for any structure. This could be a wooden post stuck into the ground. And you are correct the requirement for the disconnect is found in 225.31.
stickboy1375 said:Thanks for the correction, sometimes I forget to use the correct terminology...
It's kind of odd that such an installation would require grounding electrodes, but I vaguely remember thinking at the time that I couldn't come up with a better way to word the rule.infinity said:Actually this one I learned from my own mistake from an old thread that had 4 receptacles with 4 circuits on a wooden post.
georgestolz said:I think they about covered the bases on this, but there are also pictures on the FAQ on this topic.
It's kind of odd that such an installation would require grounding electrodes, but I vaguely remember thinking at the time that I couldn't come up with a better way to word the rule.