There is no spec, the spec would depend on the cable type, age, size, and length so publishing a spec would be impossible. You need to plot the values over the 15 minute test a look for the proper shape while comparing phases.
Is this an existing cable >5 years? If so you should not do a DC hipot test, it is considered destructive. A DC hipot will only tell you if you have gross installation failures, it is like going to the doctor running on a treadmill and if you dont die the doc says you are OK. A VLF AC hipot or better yet a Tan Delta test will give you a much better idea of the condition of your cable. Refer to IEEE 400 for details.