Greetings brothers and sisters-- My first post here though I've been using the forum as a reference for quite awhile.
My problem today has to do with lighting control. I've got a string of 400W HID fixtures on a 208V circuit that I want to switch with a T101 time clock and a photo control. Total circuit amps: 16.1A. So I plan to incorporate a contactor to switch the circuit.
The confusion arises over what kind of contactor. A 2-pole NEMA type lighting contactor such as the Square D 8903LO20 rated for 30A is almost 6 times the cost of a Definite Purpose 8910DPA42 which is both resistive and motor rated.
What I need is a plan english (that is, for a journeyman field electrician) explanation of just what a "Definite Purpose" contactor is good for. How exactly does their design differ from other types? I've read the catalog blurbs ("...ideal for heating, air conditioning, refrigeration, data processing and food service equipment"), and the the discussions here, ("DP contactors are terrible choices for one-off applications because the ratings on the labels are even more application specific than IEC ratings are, so it's really easy to misapply them and end up with damaged equipment or a fire.") But I'm still confused. Why can I use them for a motor but not a ballast? (Or do I have that wrong?)
Frankly I don't see the problem with a DP as long as I amply over rate the device. Over the years I've used them for all kinds of gizmos without any trouble. Am I just a lucky guy? Should I increase my liability insurance?
On the other side of the building I've got another 16A HID circuit switched by an Intermatic T104 (no photo control). Recommended for outdoor lighting or anything else you can think of it's been running fine for years, and considering how inexpensive they are I can't believe there's anything special about it's contacts. (Which I see are rated 40A tungsten or inductive.)
For that matter I don't see where the lighting contactor is rated for Metal Halide HIDs. It just says fluorescent and tungsten. Aside from the fact that you can order multiple poles what makes them any better than a DP?
And while we're at it what about the SCCR? An important consideration, I've been told. But how is it calculated?
Any illumination you guys can throw on this is greatly appreciated.:smile:
My problem today has to do with lighting control. I've got a string of 400W HID fixtures on a 208V circuit that I want to switch with a T101 time clock and a photo control. Total circuit amps: 16.1A. So I plan to incorporate a contactor to switch the circuit.
The confusion arises over what kind of contactor. A 2-pole NEMA type lighting contactor such as the Square D 8903LO20 rated for 30A is almost 6 times the cost of a Definite Purpose 8910DPA42 which is both resistive and motor rated.
What I need is a plan english (that is, for a journeyman field electrician) explanation of just what a "Definite Purpose" contactor is good for. How exactly does their design differ from other types? I've read the catalog blurbs ("...ideal for heating, air conditioning, refrigeration, data processing and food service equipment"), and the the discussions here, ("DP contactors are terrible choices for one-off applications because the ratings on the labels are even more application specific than IEC ratings are, so it's really easy to misapply them and end up with damaged equipment or a fire.") But I'm still confused. Why can I use them for a motor but not a ballast? (Or do I have that wrong?)
Frankly I don't see the problem with a DP as long as I amply over rate the device. Over the years I've used them for all kinds of gizmos without any trouble. Am I just a lucky guy? Should I increase my liability insurance?
On the other side of the building I've got another 16A HID circuit switched by an Intermatic T104 (no photo control). Recommended for outdoor lighting or anything else you can think of it's been running fine for years, and considering how inexpensive they are I can't believe there's anything special about it's contacts. (Which I see are rated 40A tungsten or inductive.)
For that matter I don't see where the lighting contactor is rated for Metal Halide HIDs. It just says fluorescent and tungsten. Aside from the fact that you can order multiple poles what makes them any better than a DP?
And while we're at it what about the SCCR? An important consideration, I've been told. But how is it calculated?
Any illumination you guys can throw on this is greatly appreciated.:smile: